Anyone disagree

pooteo
Member Posts: 19
I've read as much literature as I could find on placement of the diaphragm expansion tank and I can't find anything that says I can not place it where I have it. But I also can not find anything that says I can place it that far away from the spirovent.
Does anyone know if this would be a problem?
Does anyone know if this would be a problem?
0
Comments
-
It should be as close as possible to the inlet side of the circulator.
It doesn't have to be close to the Spirovent.Retired and loving it.0