Converting from Oil to HE Gas - WM unit recommendation
Jaron
Member Posts: 3
in Gas Heating
I'm in the final stages of planning my switch from my 50+ year old oil unit (it originally did coal then one of the previous owners put an oil burner in it) to a HE natrual gas unit. The contractor I want to work with - I have 2 personal references and he has the best prices - gave me quotes for weil-mclain units:
- GV90+4
- WM97 (+$1000)
- ultra105000 (+$1750)
I'm looking for opinions on these units. I was leaning towards the GV90 until I saw this thread (<a href="http://www.heatinghelp.com/forum-thread/146798/W-M-GV-90">http://www.heatinghelp.com/forum-thread/146798/W-M-GV-90</a>) so I thought I would just ask outright.
System wise, I have a small, single-zone home that I need to heat. The current system is gravity operated with copper radiators.
The ultra seams a little too pricey but I would consider it if the quality is there.
Thanks!
- GV90+4
- WM97 (+$1000)
- ultra105000 (+$1750)
I'm looking for opinions on these units. I was leaning towards the GV90 until I saw this thread (<a href="http://www.heatinghelp.com/forum-thread/146798/W-M-GV-90">http://www.heatinghelp.com/forum-thread/146798/W-M-GV-90</a>) so I thought I would just ask outright.
System wise, I have a small, single-zone home that I need to heat. The current system is gravity operated with copper radiators.
The ultra seams a little too pricey but I would consider it if the quality is there.
Thanks!
0
Comments
-
Did the contractor you want to work with
perform a heat loss calculation? How big is the house? Where is it located?0 -
@SWEI
If any of the 5 contractors did, they didn't share it with me. I doubt it was done as they didn't do all the room measurements to do so. Most of them approximated the heating need based on the existing burner and/or radiator load.
My home is ~50 years old and is located 50mi northwest of Philadelphia, PA. I have already upgraded all of the windows and have good insulation in the attic. It's about 1300 sq ft of heated living space (not counting basement or attic.)0 -
Heat loss
really needs to be done before anything is sized, proposed, or priced. At 1300 square feet, your house will need well under 50,000 BTU/hr (and quite likely less than 40,000) to heat it -- on the coldest day of the year. The most important figure for mod/con boiler sizing will be the MINIMUM firing rate of the boiler. The smaller this number, the happier the boiler (and you) will be. I'd probably recommend either a Lochinvar WHN055 (11k minimum rate) or perhaps the CDN040 (9k minimum firing rate) for a job like this. If you're set on Weil-McLain, I'd suggest looking at a WM 97+ 70 (14k minimum firing rate.)0 -
Follow
Swei's advice and have the heat loss done . These contractors may have been referred by friends but that does not make them the guy to use . Since none did a heat loss that has been confirmed .
Of the units mentioned I could only recommend the WM97 . Don't much care for either of the others . Being as you only have one zone you really want to make sure you get the smallest boiler capable of heating your load at design conditions and also one that will modulate down really low . Again , Swei's recommendation is goodYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements