iseries and transformer

I am looking at using the 4-way iseries in my setup with a ZVC406 and am looking at what my options are for the 24V power input on the iseries. Can I draw off the ZVC406 without an external transformer, utilize the R and C 24VAC (designated as being for thermostat power) on my WM97+ low voltage panel, or will I have to use an external transformer?

Comments

  • kcoppkcopp Posts: 2,626
    edited September 2013
    You can use ....

    the 24 terminals off the Taco SR control. I have done this before w/o any issues. The zvc control is a maybe. It depends on how many and much the zone valves draw off. 