Boiler delivered next size bigger than what was ordered, Keep or exchange??
Drew2100
Member Posts: 9
Hi Guys!
I ordered a Slant Fin Galaxy GXHA-120 steam boiler (120,000btu gas input, 309 sq ft) steam). My old boiler was a Hydrotherm VGA-125 (125,000btu gas input). Old boiler heated the house fine, and I calculaded the EDR of around 295 sq ft or so.
Supply house dropped off a SlantFin GXHA-160 (160,000btu gas input, 408 sq ft. steam). They charged me for the 120, and guy says I can keep the 160 for the same price.
I'm a bit concerned that the 25% or so oversizing will cost me alot extra in fuel. Is this considered way oversized, or not to worry? Would dialing back the gas pressure a bit and slightly under firing the 160 be a viable option? Or should I just tell them to pick up the 160 and give me what I ordered?
Thanks for your help!
I ordered a Slant Fin Galaxy GXHA-120 steam boiler (120,000btu gas input, 309 sq ft) steam). My old boiler was a Hydrotherm VGA-125 (125,000btu gas input). Old boiler heated the house fine, and I calculaded the EDR of around 295 sq ft or so.
Supply house dropped off a SlantFin GXHA-160 (160,000btu gas input, 408 sq ft. steam). They charged me for the 120, and guy says I can keep the 160 for the same price.
I'm a bit concerned that the 25% or so oversizing will cost me alot extra in fuel. Is this considered way oversized, or not to worry? Would dialing back the gas pressure a bit and slightly under firing the 160 be a viable option? Or should I just tell them to pick up the 160 and give me what I ordered?
Thanks for your help!
0
Comments
-
Boiler
Exchange it. You are right about your concerns. They did not do you any favors.0 -
ship it!
I'm oversized by about that amount and it causes the boiler to short cycle even with aggressive main vents, low psi gauge, etc, It's too big. Send it back like JStar says.There was an error rendering this rich post.
0 -
Sendinding it back
That's what I figured. They are oicking up the 160 and exchanging it today. Plus the 120 is around 100lbs lighter, my back and cellar stairs will appreciate that.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements