SYSTEM PRESSURE --need assistance,
bob young
Member Posts: 2,177
TEN STORY RESIDENTIAL BLDG. two pipe h.w heating system w/ steel pipe & slant fin baseboard radiation. what would recommended . system pressure & pressure relief valves. two weil-mclain cast iron boilers [1,632,00 btu ] each. conventional closed expansion tank on roof . radiation have self -bleeders.
0
Comments
-
Pressure
You'll need about 45 psi cold fill to reach the top of the highest radiator. Add a little safety margin and call it 50. The relief valve will then need to be 75 psi, if the boilers can handle that pressure.0 -
YSTEM PRESSURE --need assistance,
thanx for the speedy response, joe is there a formula or figure roughly 5# every ten ft. storey height. have not done any multi story jobs in over twenty or thirty years. new acct. i picked up with nothing but problems but i will prevail !! thanx again. bob young nyc lic. plbr.0 -
.434 PSI per vertical foot of elevation...
Plus 5 PSI.
METhere was an error rendering this rich post.
0 -
SYSTEM PRESSURE --need assistance, thanx mark
thanx mark. been a while , hope all is well with you. do you concur with the 75 # relief valve ? just want to do some quick preliminary research before i jump into this job. need to refresh my memory a little been doing mostly plumbing & residential gas & steam work lately. friend of mine asked me to get involved with this job so you know we can never turn down a challenge !! are the self bleeders a potential problem on the radiation . i think they also have some spiro vents on some of the risers but i have not seen that yet. thanx again. bob0 -
10 story system
Were there any particular problems with this system, which you need to solve?
Some Dawn detergent added to the water may get the air out. As it would be difficult to know how much to add, some sort of port could be piped in to enable adding the detergent, or any other chemical without draining down part of the system.--NBC0 -
pressure
Sounds like the good old systems , compression tanks allowed somewhere for the air to go, what do you mean by self bleeders, if they are auto air vents they should be valved off after initial fill of systemThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements