Which T&P Valve?
Options
Javelin
Member Posts: 158
Heating Gurus,
I have a Triangle Tube Prestige 250 boiler hooked up to a Smart 40 Indirect Hot water heater. Which T&P relief valve am I supposed to use? The manual seems to have two suggestions - one based on tank size, the other on BTU - but they differ:
----
Determine T&P relief valve size by the follow- ing specifications, unless they conflict with local codes:
- TR 20/30/36/45 - SMART 20/30/40/50: 3/4”NPT with an AGA Rating of 100,000 BTU/hr. (Watts 100XL-8 or equivalent).
- TR 60/80/100/120 - SMART 60/80/100: 3/4”NPT with an AGA Rating of 200,000 BTU/hr. (Watts 40XL-8 or equivalent).
----
Also, the Watts 100XL-8 is about $14 from PEX supply while the Watts 40XL-8 is about $130.. Why is there such a difference in price? Something I'm missing?
THANK YOU IN ADVANCE!
I have a Triangle Tube Prestige 250 boiler hooked up to a Smart 40 Indirect Hot water heater. Which T&P relief valve am I supposed to use? The manual seems to have two suggestions - one based on tank size, the other on BTU - but they differ:
----
Determine T&P relief valve size by the follow- ing specifications, unless they conflict with local codes:
- TR 20/30/36/45 - SMART 20/30/40/50: 3/4”NPT with an AGA Rating of 100,000 BTU/hr. (Watts 100XL-8 or equivalent).
- TR 60/80/100/120 - SMART 60/80/100: 3/4”NPT with an AGA Rating of 200,000 BTU/hr. (Watts 40XL-8 or equivalent).
----
Also, the Watts 100XL-8 is about $14 from PEX supply while the Watts 40XL-8 is about $130.. Why is there such a difference in price? Something I'm missing?
THANK YOU IN ADVANCE!
0
Comments
-
Neither one
Here in California, you have to use a relief valves rated higher than the input rating of the boiler.
Look at this chart (over 200,000 BTU) for correct sizing:
http://media.wattswater.com/F-SF.pdf
As far as the higher price, it's probably related to their insurance costs and not the manufacturing costs.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements