Boiler selection / contractor selection
Options
Dsisson
Member Posts: 92
OK, I've had 3 different contractors come and take a look. By my calculations, I need 235 SF of radiation.
Contractor 1 counted the radiators and gave a quote. He's low, and I won't hire him because he didn't size the radiation. He quoted a Pennco 1604, which has 283 SF of radiation. The next size smaller Pennco would be too small.
Contractor 2 actually sized the radiators, but I don't have a quote yet.
Contractor 3 didn't even count the radiators, but seemed to understand that near boiler piping was critical. He quoted a Utica PEG-112EID, which has 292 SF of radiation. The next size smaller would be too small at 195 sf
I don't think I want to hire #1 or #3. But I am wondering about boiler sizing and also brand selection. I'm wondering if I want to go one size smaller than these guys are quoting - for example 195 SF of radiation when I need 235 - or do I want to use the size they are suggesting (be a bit large).
Also, what about Pennco or Utica? I haven't heard any reviews of Pennco, and some people seem to like Utica and some don't. For what it's worth, contractor #3 was badmouthing Burnham and also Weil McLain. This is a gas fired boiler.
Thanks in advance and anyone who can suggest a good contractor in the Providence RI area would be helpful!
Contractor 1 counted the radiators and gave a quote. He's low, and I won't hire him because he didn't size the radiation. He quoted a Pennco 1604, which has 283 SF of radiation. The next size smaller Pennco would be too small.
Contractor 2 actually sized the radiators, but I don't have a quote yet.
Contractor 3 didn't even count the radiators, but seemed to understand that near boiler piping was critical. He quoted a Utica PEG-112EID, which has 292 SF of radiation. The next size smaller would be too small at 195 sf
I don't think I want to hire #1 or #3. But I am wondering about boiler sizing and also brand selection. I'm wondering if I want to go one size smaller than these guys are quoting - for example 195 SF of radiation when I need 235 - or do I want to use the size they are suggesting (be a bit large).
Also, what about Pennco or Utica? I haven't heard any reviews of Pennco, and some people seem to like Utica and some don't. For what it's worth, contractor #3 was badmouthing Burnham and also Weil McLain. This is a gas fired boiler.
Thanks in advance and anyone who can suggest a good contractor in the Providence RI area would be helpful!
0
Comments
-
RI Steampro
Hi- You might want to contact Steve Gronski, He's listed in "Find a Contractor" at the top of this page and his website is: http://www.gronskiplumbingandheating.com/
- Rod0
This discussion has been closed.
Categories
- All Categories
- 85.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 424 Carbon Monoxide Awareness
- 73 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 130 Geothermal
- 160 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 885 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements