Condensate switch failures (Posting here because you folks use these pumps a lot)
Cold in Baltimore
Member Posts: 14
This is the third microswitch failure on a Little Giant condensate pump. The last one is less than one year old.
The pump is for a HE boiler and a dehumidifier.
I'm getting tired of servicing this...
What do you recommend?
How about replacing the switch with a reed switch and solid state relay?
I saw a pump without a switch at RE Michael's but I cannot find it online. Anyone have any experience with them? I think it uses a capacitive sensor.
The pump is for a HE boiler and a dehumidifier.
I'm getting tired of servicing this...
What do you recommend?
How about replacing the switch with a reed switch and solid state relay?
I saw a pump without a switch at RE Michael's but I cannot find it online. Anyone have any experience with them? I think it uses a capacitive sensor.
0
Comments
-
Switchless
Have a couple of these out there for about a year now.
http://www.diversitech.com/Product-Line?id=a0jC0000005QEykIAG
No complaints thus far. Nice unit,0 -
Diversitech
Although I have never used that exact model I have two of their floatless cube units under my mini spits, I have had quite a bit of trouble with both of them, one more than the other. Evidently they try to match pump speed with condensate flow, that produces a lot of noise on a continual basis. Interestingly,I just purched a new Aspen mini white pump that is located externally to the mini split, very similar to the Diversitech style but it uses a standard float and is designed to be easily cleaned. After a delay in this pump arriving it was explained to me that Diversitech just purchesed that division of Aspen. Another problem with the floatless units is they use a computer dc supply that draws current all the time, probably more on standby than a normal float style uses all year.
Also not to bash on Diversitech but I had one of their standard condensate pumps(the red one) with the float fail. The closed cell foam they use for the float actually became water logged under a condensing boiler and shut down the boiler. I was given another pump and so far so good.0 -
Clearvue
We seemed to have a lot of problems with the standard Diversitech and the Clearvue pumps. Went back to the Little Giant NextGen which R E Michel has at a great price. No more issues.0 -
Condensate pump on a Condensing Burner
The condensate from a condensing gas appliance is acidic and some condensate pumps are not rated for that use. If you are using a non-rated pump, you will see failures. So far that and a lack of maintenance are the only common problems I see with any regularity.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements