Sizing for a Steam replacement boiler. will this work?
Joseph_4
Member Posts: 293
Hi. I have a customer with a steam system with 19 cast iron radiators whose edr comes out to 765 sq. foot. The boiler I'm looking at for technical reasons is rated for 733 sq. feet. I know from Dan's "Lost Art" that when sizing steam systems you go according to the connected load. However, I know from doing a heat loss that the radiators in each room in the house are grossly oversized. so do i care if say the last section on each radiator doesn't get hot. even if it does turn back to water before it gets hot. its overkill anyway?
Any input would be greatly appreciated
Thanks
Joe
Any input would be greatly appreciated
Thanks
Joe
0
Comments
-
Steam
You want to cover the radiation load. HOWEVER, most manufacturer's sizing charts are based on a 33% pickup factor. If the piping is insulated, I only add 15%. Partially insulated, I add 20-25%. So, the next question is.....is the system piping insulated?0 -
the pipes are insulated
Hi. yes the pipes are insulated in the basement. but the 765 and 733 is after you subtract the 33% pick up factor. In this house when i multiply 240 x 765 i get 183,600 btu and if i multiply that by 1.33 i get 244,188 btu. A crown ksz200 says the doe heating capacity is 235mbh and its net rating steam square foot is 733.
or are you saying if pipes insulated i can multiplty 183,600 by say 20% or 1.20 and then i get 220320 btu in which case this boiler will do the job?0 -
Boiler
I would choose the KSZ200. Or you could install 2 KSZ090's and stage them for incredible system efficiency and fuel savings.0 -
Thanks for your input jstar
i appreciate your input
joe0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements