Indirect temps
Jack
Member Posts: 1,049
What temps do you generally set your indirects? Do you add tempering valves on them?
0
Comments
-
Indirect temperature
125F
If the capacity of the indirect is sufficient for household needs, then 125F is fine. If not, we set the indirect higher (150F) and install a tempering valve.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Always do
I've been taught to always put a mixing valve even on water heaters. But I do open up all the way and leave aqua stat at 130 tops0 -
Always
I set them at 140-150 and install a tempering valve on all my indirects.There was an error rendering this rich post.
0 -
Mixing Valve
If you decide to use a mixing valve, I like the new one by Honeywell. It's very easy to install.
Edit: Sorry, this is made for a standard, atmospheric water heater and may not be set up properly for an indirect.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
two thoughts
120- 125F takes care of the code requirement and lessens scald potential. But Legionella can be an issue with low storage temperatures.
140F or higher will handle the legionella concern, but a listed mixing valve must be installed to protect against scald potential.
It takes more energy to warm the water to 140F, then blend it with cold to useable temperatures around 115F.
Lower operating temperatures extend the tank life. Lower temperatures precipitate less minerals from the water.. Also less insulation and standby loss, at lower operating temperatures.
More and more European countries are requiring tanks, especially solar tanks, be elevated to 140F for a 1 hour period every 24 hours. A good compromise solution, I suppose.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements