Hot Water Boiler Extrol and Fill Valve

Hi,
Could someone tell me if the pressure setting of the fill valve (Watts SB1156F) and the charge pressure of the Extrol tank should be the same or how should it be set up. The valve came preset to 15 psi and the tank (size 60) is precharged to 12.
The house is a two story cape with only one zone.
Thanks,
Dan
Could someone tell me if the pressure setting of the fill valve (Watts SB1156F) and the charge pressure of the Extrol tank should be the same or how should it be set up. The valve came preset to 15 psi and the tank (size 60) is precharged to 12.
The house is a two story cape with only one zone.
Thanks,
Dan
0
This discussion has been closed.
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 561 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
And set to the design pressure of the system. 15# is about right for a two story house -- unless the distance from the low point of the system to the high point is over 23 feet.
Design pressure (minimum) = distance between those points times 0.434 plus 5 pounds.
No more dripping relief valve.