I am not going to preach to you guys today , just-ed wanted to pass on some good news today.
I recently got involved with a large church that has had several problems for the last 7 years and got called in to help. I was working on a 20 ton split not going to call its name . First let me tell you good folks some facts about the system. Somebody decided to replace the condenser on a 45 year old air-handler
I found through some serious investigation they put a 20 ton unit on a 15 ton coil lmao rotf. I got my good friends at the COIL COMPANY out of Poali, Pa. to build me a coil and by the way these guys are great.Ask for Jack Lyoins
I recovered 69lbs of r-22, put a new tx valve,new drier and new pump down valve, pressurized system to 400 psi and then evacuated system down to 450 microns I installed 59lbs of 421a and 6 ounces of poe oil because of the vertical rise and that is what is recommended. The pressure were great, great oil return, great discharge and suction temps. Great sub-cooling temps. Best news of all is the ac unit coled better than it did when it first was installed. Thank you Ken Ponder (RMS FIRST CHOICE DISTRIBUTOR )
PEACE BE WITH YOU
DAVID C. BROOME
I recently got involved with a large church that has had several problems for the last 7 years and got called in to help. I was working on a 20 ton split not going to call its name . First let me tell you good folks some facts about the system. Somebody decided to replace the condenser on a 45 year old air-handler
I found through some serious investigation they put a 20 ton unit on a 15 ton coil lmao rotf. I got my good friends at the COIL COMPANY out of Poali, Pa. to build me a coil and by the way these guys are great.Ask for Jack Lyoins
I recovered 69lbs of r-22, put a new tx valve,new drier and new pump down valve, pressurized system to 400 psi and then evacuated system down to 450 microns I installed 59lbs of 421a and 6 ounces of poe oil because of the vertical rise and that is what is recommended. The pressure were great, great oil return, great discharge and suction temps. Great sub-cooling temps. Best news of all is the ac unit coled better than it did when it first was installed. Thank you Ken Ponder (RMS FIRST CHOICE DISTRIBUTOR )
PEACE BE WITH YOU
DAVID C. BROOME
0
Comments
-
TXV
What was the old vs. new TXV's? How hi is the vertical riser? Liquid line FD only ? The comp has an oil eye? Whats the warmest ambient this unit has run at?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements