combine tankless flues
keyote
Member Posts: 659
Ive got a rental on top floor that i have started to build with a rheem 64 tankless unit under a future stair behind the bath room. its 3/5 vent goes right out a 13" brick exterior wall. directly under floor, below im building my own unit with another bathroom and its own rheem 64 Id like to gang the two flues together and have only one wall penetration but rheem and metal fab are just too stupid to reach or answer questions in any way that instills confidence that some idiot is reading from a script in fact they dont even answer this question and refer you to a paid service. anyway im aware of the issues but also think ive seen this done on large commercial jobs any ideas?
0
Comments
-
0
-
tankless flues
dont see anywhere on the link the question is addressed. i realize of course they must be fan powered but a backdraft damper might solve that0 -
Appliiances come with installation instructions
Read it!
"The water heater must be vented to the
outdoors as described in these instructions.
DO NOT connect this water heater to a
chimney. It must be vented separately from
all other appliances."
chimney. It must be vented separately from
all other appliances."
"The water heater must be vented to the
outdoors as described in these instructions.
DO NOT connect this water heater to a
chimney. It must be vented separately from
all other appliances."
chimney. It must be vented separately from
all other appliances."
WARNING "For multiple unit installation, a minimum
distance between vent terminations must be maintained to
prevent recirculation of vent gases. Maintain a center-to-center
distance between vent terminations of 19 inches (48 cm) for two
unit installation. Maintain a center-to-center distance between
vent terminations of 21 inches (53 cm) for three or more unit
installation." "For multiple unit installation, a minimum
distance between vent terminations must be maintained to
prevent recirculation of vent gases. Maintain a center-to-center
distance between vent terminations of 19 inches (48 cm) for two
unit installation. Maintain a center-to-center distance between
vent terminations of 21 inches (53 cm) for three or more unit
installation."
The life you save may be your own0 -
Eternal
Check out this link. The Eternal brand of tankless water heaters can apparently have a common vent.
Rob
http://www.heatinghelp.com/forum-thread/141150/Four-Hybrid-Eternals-for-a-Restuarant-photos80 -
So can many other tankless brands
As long as they're serving the same domestic water system0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements