2 Pipe Steam! Trap placement?
flash996
Member Posts: 2
This is a two pipe system, these are in the basement. Was wondering if anyone has seen this done and how it affects my B dimension ? I would say the boiler water line is about a foot bellow the lowest elbow you see and is a wet return at that point which enters into an F&T at the boiler about the height of the bottom of the wall trim. These heat well but there are other issues in the system I am trying to resolve and ws wondering if they could be part of the problem?
0
Comments
-
That was probably an Illinois Engineering Co. system
I've seen their systems set up like that before. The return connection from the radiators does allow steam to pass, assuming there's no water seal or other device to stop it further down the line, so it's not strictly a "B" dimension. The traps in this case only serve to direct the air back to the dry return.
You say there is an F&T trap at the end of that wet return? Where does it discharge to?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Discharge
goes into a boiler feed tank that was recently installed and is driving the owner crazy. he has asked me to remove it .. I am doing all I can to be sure that if I do the system is going to work properly..0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements