Hi I have a steam boiler job that is being converted to a hot water boiler job. I know oventrop makes a valve for this type job. Does anyone else make one?
0
Comments
-
You talking
thermostatic radiator valves? Try Danfoss.
I'd like to hear more about your steam to hot water conversion.
- Has the system been pressure tested for leaks?
- Are there room-by-room heat loss calculations and radiator output numbers to see how the radiators will perform?
I'm just curious because I've been tempted many times to do the same thing.
Alan8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
This might well be the Oventrop
But someone here linked to it awhile back and I saved the PDF http://www.hydronicalternatives.com/getattachment/16707372-633d-4cff-a1c4-357fcfcaa8ef/Steam-to-Hot-Water-Conversion-Valve.aspx0 -
" Has the system been pressure tested for leaks?"
" Are there room-by-room heat loss calculations and radiator output numbers to see how the radiators will perform"
If not, I hope Bob has a good lawyer. I've seen too many messed-up conversions.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Good lawyer-or good contract?
In this case the contract of installation would be the most important. The problems of leaks may not show up right away, but a few years down the road. Therefore the installation contract should specify the length of warantee, so thet a leak in 2 years is not covered, either for it's repair, or it's damage.
This should not be in the fine print, but an up front clause, to prevent annoying calls from the customer,or his insurance co.
A pressure test would be a good idea in this case, to pinpoint any weak spots in the piping.--NBC0 -
Steam to hot water
Hi thanks for the input. I am a P&H wholesaler salesman and I have a customer doing this steam to hot water conversion job. It is a church job. We will do a heat loss. He will be removing all old black steel piping and he does water test the old cast iron radiators and the radiators will be flushed out before water system is piped in. He will also be installing a dirt separator on the system. He is telling the church if they want to do this conversion and the old radiators end up leaking down the road he is nor responsible for that. The church is the one who wants to convert steam to water. Any other input is helpful.0 -
Knunclehead
In Steamheads words, the system has probably been "knuckleheaded" and the church has banging during their services. It would be cheaper for the church to find a new repair guy than to replace the system.
Rob0 -
other input
clean, flush, repeat. Repeat again after a month or so. Rhomar 9100/9250 works well. Treat the fill water after that.
Check back in a year and be prepared to flush again. Re-treat.
Caleffi Dirtmag was made for this.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements