return line depth in 275 tank
hh409
Member Posts: 14
in Oil Heating
at what depth should the return line be inserted in a 275 in basement tank? i think it is currently inserted about 1/3rd off the bottom of the tank. is the depth critical? am i correct in assuming that it should be deep enough to always be submerged in oil so it won't loose prime? if not is the worst that could happen that the prime will be lost?
thanks
thanks
0
Comments
-
Why?
Why are you using a 2 pipe system? It only creates high vacuum, and plugs filters sooner. You won't lose prime if it is not down to the bottom. It should be close to the bottom though, especially if it is an underground tank. Sometimes the return line needed to become a feed line.0 -
Agree with Bill
If it's a basement 275 and the oil burner is lower than the tank , you don't need to pump all that extra oil with a 2 pipe setup . Even if the line is from the top of the tank . And I agree with Bill about the level of both oil lines . You might need to switch the the 2nd line someday if the first line fails .0 -
return line depth in 275 tank
I agree with these answers! You do NOT need a return line from a basement tank! But if you insist run feed and return to close to the bottom with the return about 2" higher than the supply.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements