Formulas for heat-loss calculations

Can anyone confirm any of these formulas for me?



BTU losses = sq. ft. X (1/R) X temperature difference in F



Losses to ceilings are 15% higher due to radiation losses?



BTU losses via infiltration = room volume Cu. Ft. X .018 X temperature difference in F X A



A= .2 for well sealed rooms, ranging to .5 for poorly sealed rooms



Thanks

Comments

  • JStar
    JStar Member Posts: 2,752
    Heat loss

    They might be right...for one specific type of home. Which home? Who knows?



    Better do a real Manual J.
  • CMadatMe
    CMadatMe Member Posts: 3,086
    Heat Loss for An Outside Panel

    Ti-To/R-Value = Btu/hr Sqft



    Ti = Temp Indoor

    To= Temp Outdoor

    R-Value = Self Explanitory

    There was an error rendering this rich post.

  • Zeffern_Cochrane
    Zeffern_Cochrane Member Posts: 12
    Puzzled

    Thanks Chris that yields the same result as my first formula so thats one down probably a few more to go.



    Jstar your response intrigues me. Another post in a different sub category suggested that the heat loss requirements in a home heated with radiant floor heat would be less then some outer home with a different kind of heating system (Forced Air I presume). I have a heat loss calculation done by a hydronic heating supplier that came up about 15,000 higher then what I calculated on one of those web calculators. I have tried several and with just simple square box designs came up with a different answer on each one. That has led me to trying to develop a spreadsheet to come up with numbers that I can have confidence in.



    One of the things I stumbled across was this factor of infiltration and apparently this has a huge factor in the final results. I believe that the calculations done by the supplier are on the high side of things, and why not if you can sell a 200,000 boiler to someone who needs a 150,000 boiler all the more profits to you.



    Can anyone suggest resources that may lead me to discover the true effects of infiltration on heat loss. Were building the house our selfs so we are achieving a very good vapour barrier but I am sure that there will always be a lot of losses through tiny cracks in doors and window gaskets ect.



    Thanks
  • CMadatMe
    CMadatMe Member Posts: 3,086
    Suggest You Purchase

    Modern Hydronics 3rd Edition avail here in the store. Lays it out quite nicely. Infiltration is the main reason why a radiant loss is less then a fin tube or air loss. The more the convection the more the infiltration loss. Pretty basic stuff.

    There was an error rendering this rich post.

  • NRT_Rob
    NRT_Rob Member Posts: 1,013
    not really true.

    more PRESSURE differential more in/exfiltration. not more "convection". If you dump 500 cfm in a bedroom with no way out, you will drive exfiltration. ditto for a room with a return and no way for air to get to it.



    taller buildings with stack effects is more in/exfiltration.



    more holes of course = more infiltration.



    radiant loads can be lower because duct losses can be lower. you might drive less infiltration but it's not inherent to the application of forced air to have higher infiltration.



    zeff, your formula are correct but your inputs are still where the magic is. GIGO my friend. you have some heavy reading ahead of you on that front to get good numbers.
    Rob Brown
    Designer for Rockport Mechanical
    in beautiful Rockport Maine.
  • Zeffern_Cochrane
    Zeffern_Cochrane Member Posts: 12
    edited April 2013
    Thanks

    Thanks Chris & Rob good advice I am sure maybe I am getting to hung up on this BTU stuff and should just go with what the supply house guy says. In the end I will need someones stamp of approval for the building inspector so it does not matter what I think it will be up to who ever can certify that the system meets design temperature conditions. I looked at the book section, seems like it covers quite the range of all the things that I want to know. And probably a lot that I don't need or shouldn't worry about for a one house build. Though I have been contemplating a couple of those books from Dan that were way less expensive and probably more appropriate to the kinds of things I really should know. Books like the installers guide and pumping away.



    Thanks



    One more thing Rob can you send me a larger picture of that one in your signature it looks really nice I would like to look at it more closely.