Stupid question here but can't seem to figure this out.
Dan_40
Member Posts: 15
Went to look at a nuisance call today. Former customer but I did not install or work on the system. Old(1972) weil Mclein gas fired hot water boiler. Did not see an old tankless on it. Has a high/low aquastat controlling boiler and zone 1. since then zones 2 and 3 have been added. zones 2 and 3 are single zon relays for each. all zones are baseboard. Complaint was that 2nd floor is heating all the time. Customer has shut off all t-stats as well as all switches on the boiler. no chance that pumps are running. Zone 1 is 1st floor, zone 2 is 2nd floor and zone 3 is basement. Upon arrival noticed that all tstats are off. second floor heat is migrating and all baseboard is hot. Figure a bad flow check. go to boiler room and see all switches in the off position, yet all supply pipes too hot to touch. second floor return pipe too hot to touch. basement and first floor returns are cold. figure bad flow checks. look at hi/low aqaustat and realize it is set for 180 hi and boiler is firing to 220. It is a millivolt system.
Am I dealing with a bad aquastat and three bad flow checks all at the same time? or am I missing something?
Am I dealing with a bad aquastat and three bad flow checks all at the same time? or am I missing something?
0
Comments
-
No such thing as a stupid question
First thing I'd do is see if there's heat transfer grease in the aquastat well. There's no reason it should be getting that hot.
Do the circ relays all have dry contacts to start the burners?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
One possiblity...
Let's assume the aquastat is malfunctioning for some reason. Is it possible the check valve for Zone 2 never closed. It is the tallest zone, creating the greatest potential for a gravity induced pressure delta due to temperature differences. The other zones' supply lines could be hot purely from heat conducting though the copper across the check valves.0 -
Bad flow check for 2nd floor
You most likely have a bad flow check for the 2nd floor. If it is over heating there, then the t-stat is satisfied and the circulator never comes on. And if the other circulators come on you would get reverse flow through the second floor zone. That is why the second floor return is hot. Bad flow checks are very common, but not three bad at the same time. Hope this helps. Mike.0 -
It's to old to worry about
First of all it’s a 40 + year old boiler is any time spent repairing and not replacing is a waste. But if the customer insists then I would first make sure he’s gonna pay regardless of results. Then I would start by disconnecting aqua stat and cooling down boiler and starting top floor zone only. Let boiler fire up to maybe 160* and see what happens in the other 2 zones. If other zones are fine most likely aqua stat if not you might be able to check by feel whats up with the other zones.0 -
return line or supply line
i would let the system cool of and than check what side of the check gets hot first0 -
return line or supply line
i would let the system cool of and than check what side of the check gets hot first0 -
flow
First of all YOU have to see if the aquastat is bad. Powerpile or 24 volt can still have a problem. When the burner is firing remove one wire off of the aquastat to see if the burner shuts down ( it may take a few seconds to respond to open or close) If it doesn't then something is wrong with the wiring, gas valve or aquastat relay controller.
You will have to figure out where the circuit is closed.
As for the second floor getting too hot. The flow checks may be working just fine BUT normal operating temperature is 180* - 220* is possibly over powering the 2nd floor flow check. Get the temps back down to normal and see what happens.0 -
Happened to Me
"And if the other circulators come on you would get reverse flow through the second floor zone."
In my own home, scratching my head until I figured it out.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements