Radiant off steam boiler
Steve Garson_2
Member Posts: 712
OK, I know this is not best practices, but...
The Combi-core water heater that heats my addition with radiant heat
(15,000BTU heat loss) needs replacement. This will be my third and I
want to do something that will last. The heat load is rather small, so a
dedicated boiler seems a bit expensive and unnecessary. My WM-SGO-3
steam boiler has an Everhot heat exhanger tank to heat a small hydonic
loop (10,000BTU heat loss.
I was thinking that it might be more cost effective to have another
Everhot, or use the same one, to heat the radiant loop. Any thoughts?
Steve Garson
Boston, MA
The Combi-core water heater that heats my addition with radiant heat
(15,000BTU heat loss) needs replacement. This will be my third and I
want to do something that will last. The heat load is rather small, so a
dedicated boiler seems a bit expensive and unnecessary. My WM-SGO-3
steam boiler has an Everhot heat exhanger tank to heat a small hydonic
loop (10,000BTU heat loss.
I was thinking that it might be more cost effective to have another
Everhot, or use the same one, to heat the radiant loop. Any thoughts?
Steve Garson
Boston, MA
Steve from Denver, CO
0
Comments
-
how does the steam boiler
compare to the EDR of the steam emitters? Being a SGO3 it may not have the power to maintain steam and heat the zone. Heat loss calculations and radiator surveys need done. If you have the btu's then you can come off the same everhot and use a 3 way mixing valve for the radiant zone.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements