Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Heat Loss From Usage
JofG
Member Posts: 3
I am in the process of converting from oil to to natural gas for home heating and hot water (I live near Philadelphia). I have decided to go with a high efficiency mod/con boiler but have received wildly divergent estimates for sizing from potential contractors (59k to 211k!). I have attempted to estimate the heat loss but am not confident in my estimates because I am missing accurate insulation information.
It hit me that I should be able to do better than estimate the heat loss like this by finding my heat loss from actual usage. I know exactly how much oil I have used and the number of degree days for this period. I can reasonably estimate the efficiency of my old oil boiler (Columbia FT-6165C) and make a guess at how much of the usage is for hot water (I have a summer/winter hookup). Worst case I can ignore the hot water and get an upper bound estimate.
Listed below is the information from the spreadsheet I created for this. I have never done anything like this before and want to know if I am missing something? Also am I correct in assessing that this is actually better than a traditional heat loss calculation since it is measuring my actual usage?
Thanks to anyone who can shed some light on this.
--------------------------------------------------------------------------
Measured Heat Loss
The tank was full on 12/30/2010 and then again on 3/5/2013. So the oil delivered between these dates is exactly what we used.
Total Gallons Used..............2,921
BTU's Per Gallon.............140,000
Gross BTU's.............408,884,000
Boiler Efficiency.....................0.82 (estimate)
Net BTU's.................335,284,880
% BTU's For HW...................0.05 (wild estimate!)
Heating BTU's..........318,520,636
Degree Days.....................11,206
Degree Hours.................268,946
BTU's Per Hr Per Degree...1,184
Delta T For Coldest Hour........54 (68 - 14)
Max Heat Loss Hour........63,954
It hit me that I should be able to do better than estimate the heat loss like this by finding my heat loss from actual usage. I know exactly how much oil I have used and the number of degree days for this period. I can reasonably estimate the efficiency of my old oil boiler (Columbia FT-6165C) and make a guess at how much of the usage is for hot water (I have a summer/winter hookup). Worst case I can ignore the hot water and get an upper bound estimate.
Listed below is the information from the spreadsheet I created for this. I have never done anything like this before and want to know if I am missing something? Also am I correct in assessing that this is actually better than a traditional heat loss calculation since it is measuring my actual usage?
Thanks to anyone who can shed some light on this.
--------------------------------------------------------------------------
Measured Heat Loss
The tank was full on 12/30/2010 and then again on 3/5/2013. So the oil delivered between these dates is exactly what we used.
Total Gallons Used..............2,921
BTU's Per Gallon.............140,000
Gross BTU's.............408,884,000
Boiler Efficiency.....................0.82 (estimate)
Net BTU's.................335,284,880
% BTU's For HW...................0.05 (wild estimate!)
Heating BTU's..........318,520,636
Degree Days.....................11,206
Degree Hours.................268,946
BTU's Per Hr Per Degree...1,184
Delta T For Coldest Hour........54 (68 - 14)
Max Heat Loss Hour........63,954
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements