psi and ft/head
mark schofield
Member Posts: 154
Is there a liniar correlation between the psi supply and return difference across the circulator when running ( closed loop hydronic baseboard) and the ft of head in a system? does the psi difference translate into a specific number for head? thanks
0
Comments
-
-
psi and ft/head
thanks0 -
Or
Just multiply the psi difference by 2.310 -
pump head
Here is some info for pump diagnostics
(1) To determine pump shut off head. Start pump with discharge valve closed, record the diff. between the discharge and suction press. multiply by 2.31 equals TDH in ft. This can be used with a pump curve/applic. to determine impeller size if not known. Run pump only long enough to get readings, make sure you have accurate press. guages.
(2) To determine operating head open discharge valve record discharge minus suction x 2.31 this reading in ft. can be used on pump curve to determine pump operating point. make sure in both cases if you are using a triple duty valve for shutoff that you mark setting.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements