Cold Start Boiler questions

Options
Hey everyone. Just a quick thank you to all the people on here who take time out of their days and schedules to answer questions from us younger guys in the trades.

The company I work for is doing alot of work for the Gas company doing gas conversions. Where I live the Gas company offers very good deals on The Burnham alpine modulating/condensing boiler so thats what we install most. My question is in regards to maximizing efficency of the boiler by extracting as much heat as possible from the boiler so that heat isn't lost to the surrounding air in between cycles. In the attempt to lessen standby energy loss is there any way the boiler could be configured  to circulate whatever hot water that was left over after the call for heat through the indirect water heater so any leftover heat could be collected and used for DHW and not simply lost to its surrroundings.

Now im not sure if  this is something that the boiler is pre programmed to do this kinda like a post purge or if it is something that has to programmed or wired up kind of like the DHW being priotized on the control board.

thanks

Comments

  • tangled in wires
    tangled in wires Member Posts: 23
    Options
    answered my own question duhhh

    Answered my own question

    I guess sometimes we think to hard From the Alpine operation manual



    an indirect water heater thermostatcan be connected

    between terminals 2 and 4 on the terminal strip. When

    this thermostat closes, the central heating circulator will
    an indirect water heater thermostat
    can be connected

    between terminals 2 and 4 on the terminal strip. When

    this thermostat closes, the central heating circulator will


    be turned off and the DHW circulator will be turned on.
  • tangled in wires
    tangled in wires Member Posts: 23
    Options
    answered my own question duhhh

    Answered my own question

    I guess sometimes we think to hard From the Alpine operation manual



    an indirect water heater thermostatcan be connected

    between terminals 2 and 4 on the terminal strip. When

    this thermostat closes, the central heating circulator will
    an indirect water heater thermostat
    can be connected

    between terminals 2 and 4 on the terminal strip. When

    this thermostat closes, the central heating circulator will


    be turned off and the DHW circulator will be turned on.