Cold Start Boiler questions
tangled in wires
Member Posts: 23
Hey everyone. Just a quick thank you to all the people on here who take time out of their days and schedules to answer questions from us younger guys in the trades.
The company I work for is doing alot of work for the Gas company doing gas conversions. Where I live the Gas company offers very good deals on The Burnham alpine modulating/condensing boiler so thats what we install most. My question is in regards to maximizing efficency of the boiler by extracting as much heat as possible from the boiler so that heat isn't lost to the surrounding air in between cycles. In the attempt to lessen standby energy loss is there any way the boiler could be configured to circulate whatever hot water that was left over after the call for heat through the indirect water heater so any leftover heat could be collected and used for DHW and not simply lost to its surrroundings.
Now im not sure if this is something that the boiler is pre programmed to do this kinda like a post purge or if it is something that has to programmed or wired up kind of like the DHW being priotized on the control board.
thanks
The company I work for is doing alot of work for the Gas company doing gas conversions. Where I live the Gas company offers very good deals on The Burnham alpine modulating/condensing boiler so thats what we install most. My question is in regards to maximizing efficency of the boiler by extracting as much heat as possible from the boiler so that heat isn't lost to the surrounding air in between cycles. In the attempt to lessen standby energy loss is there any way the boiler could be configured to circulate whatever hot water that was left over after the call for heat through the indirect water heater so any leftover heat could be collected and used for DHW and not simply lost to its surrroundings.
Now im not sure if this is something that the boiler is pre programmed to do this kinda like a post purge or if it is something that has to programmed or wired up kind of like the DHW being priotized on the control board.
thanks
0
Comments
-
answered my own question duhhh
Answered my own question
I guess sometimes we think to hard From the Alpine operation manual
an indirect water heater thermostatcan be connected
between terminals 2 and 4 on the terminal strip. When
this thermostat closes, the central heating circulator willan indirect water heater thermostatcan be connected
between terminals 2 and 4 on the terminal strip. When
this thermostat closes, the central heating circulator will
be turned off and the DHW circulator will be turned on.0 -
answered my own question duhhh
Answered my own question
I guess sometimes we think to hard From the Alpine operation manual
an indirect water heater thermostatcan be connected
between terminals 2 and 4 on the terminal strip. When
this thermostat closes, the central heating circulator willan indirect water heater thermostatcan be connected
between terminals 2 and 4 on the terminal strip. When
this thermostat closes, the central heating circulator will
be turned off and the DHW circulator will be turned on.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements