Beckett cf500 burner smith a19 series boiler
jeremiah
Member Posts: 8
Anyone have any thoughts on why this burner would be firing very hard to the point where it is almost exploding on? The heat exhanger is clean the electrode gap is good and there is good oil flow
0
Comments
-
How's the....
Draft? Excess air? Then I would check the delay valve & pump cut off, transformer, etcThere was an error rendering this rich post.
0 -
all of the above and
incoming voltage, pump pressure, Firing rate, was this an OEM package? Do you need the specs for this?0 -
Figured it out
Just wanted to thank u guys for the responses. I also wanted to say that I figured out what the problem was. I ended up going back with the manual for the burner and found out that the z dimension was off by 3/4 of an inch. I adjusted it to where it should be and it now fires off smooth0 -
"Z" Dimension:
How on earth did yo get the "Z" dimension 3/4" out? Did you loosen the placement screw to get the nozzle assembly out? Most I know don't do that. I've never seen a Beckett that I couldn't get the assembly out without touching that screw and messing up the setting. I've seen that discussion on the "Z" dimension and wondered how it could be off. I guess it is because the screw is loosened.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements