reset Wika 3psi gauge
malex
Member Posts: 106
I was installing my new Vstat and while I was disassembling the old set up I dropped my Wika 3psi gauge in the blow down bucket below. There was about an inch of water in the bucket.
When I picket it up the pointer was not at 0 but significantly below. I but it on the new assembly and it works but it seems to be 'off' by the amount the pointer is below 0 when not in operation.
I set the Vaporstat (0-4psi) to about .7psi and the gauge showed .4psi when it cut out. the difference, .3psi, is about how much the pointer is off so I assume the gauge is working.
Is there any way to recalibrate? There are some star screws on the back and flat screws on the dial but I dont want to mess with them unless I know what I am doing.
When I picket it up the pointer was not at 0 but significantly below. I but it on the new assembly and it works but it seems to be 'off' by the amount the pointer is below 0 when not in operation.
I set the Vaporstat (0-4psi) to about .7psi and the gauge showed .4psi when it cut out. the difference, .3psi, is about how much the pointer is off so I assume the gauge is working.
Is there any way to recalibrate? There are some star screws on the back and flat screws on the dial but I dont want to mess with them unless I know what I am doing.
0
Comments
-
First
Make sure ALL of the water is out of the guage. This gauge hates water which is why I modified how mine is piped in.
Once you are 100% sure its dry and not plumbed into the system you can pop the plastic lense off and turn the screw near the bottom which has a + and - on it. There should be two spots on the lense to fit a small flat head screw driver to pry it off. I do it by inserting the screwdriver and twisting. DO NOT do this with the guage installed as it will be off due a slight vacuum after the siphon.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Dry it out
Thanks Chris! I will dry it out as much as I can and pop the plastic to adjust. I am thinking it was the impact rather than the water that put it off kilter but I ll try to get any water out of there.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements