water hammer
Paul S_3
Member Posts: 1,274
im having a issue with existing boilers with water hammer by the hartford loop....i feel i can fix the problem by putting a close nipple and lowering the tee a feww inches....i have a picture where my finger is pointing that is where the water line is .....i know the piping is wrong as far as the header with no swing joint , i usually go 3 '' with the header at this size....just want some insight with this water hammer problem....thank you Paul S
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
water hammer
yup thats your problem, and the fix IS to lower the T to 2 inch below water line , and close nipple that connection0 -
Hartford
Funny thing...I've never had noise problems with a tee that was too high or too low, or even with a long nipple on the loop.
Does the water feed tie into the top of the loop? Does it make noise when it's being fed with water? When during the cycle does it happen?0 -
middle cycle
it happens in the middle of the cycle....when i feed water the hammering STOPS....there sre three more boilers to the right they are all piped identical....all 4 boilers have hammering in the same area...hartford loop....Paul SASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Water Feed:
In no way am I a steam pro. But, is that an unusual water fill or an unusual way to feed water to the boilers? Where they all do the same thing, I just wonder. The location of the water feed looks like it is above the boiler. How does it know when or how much water to add?
Is that a "normal" way to feed a steam boiler? At the top of a Hartford Loop? What happens when you shut off the water feed to the boiler. Does it stop? The fact that all four boilers do the same thing make me think that it is a piping problem with all and not just one. And someone else said that they had never seen a problem with a piping arrangement like that before. Someone re-piped recently and put the union in. Was it you or someone before you?
It sounds like it has been an on going problem. Look at how it is fed. IMO.
Interesting.0 -
I fixed
The union....it was leaking...the water feeder feeds water to the lowest minimum water when the low water cutoff calls for it....I'm getting hammering at Hartford loop in All four boilers....I believe if I drop the tees a few inches so that its at least two inches below water line and put close nipples at the loops or a wye fitting it will stop hammering...I just wanted some insight from other people if that will fix problem...do not want to do job and still get hammering.....Paul SASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Do yourself a favor
When doing the work add a drain for the wet return so you can easily get at any crud that settles there. Years from now you will be glad it's there.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
What about
Raising that a few more inches and making a Giffords loop instead?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Hammer
What pressure is it running?0 -
3 psi
It was running between three and one psi...I changed the settings to half and one and a half...I will go back Monday to check and do work....also what is a giffords loop never heard of it ...Paul SASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Gifford loop
Search for this pdf on the site HPACgiffordloop.pdf. I tried to attach it but I don't usually have any luck attaching pdf documents.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Has
anyone tried this GIFFORD loop ???....i thought you would get hammering if you attach the tee above the water line....it really doesnt explain much about why it doesnt hammer....Paul SASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements