main steam line venting questoin
EricG
Member Posts: 2
I have a 1930 2 story 2 family home with a 7 year-old oil-fired boiler. I get heating in all of the radiators in about 20 minutes. No issues with water hammer or excessive water usage. All radiators have new vari-value steam vents with the large radiators full open and the smaller, medium set close to the close position.
I recently insulated the near boiler piping and the steam hits the radiators very quickly now. Boilter pressue is registers just about zero on the gauge.
I have 2 2" steam supply mains that run from the back of the basement to the front of the house.
Each steam supply main has old Gorton No 1 air eliminators (3/8" fittings) at the front of the house where the supply mains turn 90 degrees down and join the wet return line. One of the supply mains is just getting warm to the touch and the 3 risers and radiators on this supply line are ice cold. On the 2nd supply main I was able to remove and clean the air eilimator and it is working and the piping is hot and the radiators on this supply main are getting hot.
It was difficult to remove the single old air eliminator and I am wondering if there is a way to clear / clean the other air eliminator or any other diagnostics I can do now in the middle of the heating season to try to get heat to the cold radiators. I have changed the air vents on the 3 radiators and verified tha the radiator values are operational and fully open.
Other maintenance I have done. - the hartford loop has a faucet drain at the end of the wet return near the boiler and I drained the wet return - some rusty water and then clear water after 10 minutes draining.
There are 2 additional steam mains from the boiler to the rear of the building and the
air eilimators were replaced when the boiler was changed. All the other radiators in the house except 3 are working properly.
I recently insulated the near boiler piping and the steam hits the radiators very quickly now. Boilter pressue is registers just about zero on the gauge.
I have 2 2" steam supply mains that run from the back of the basement to the front of the house.
Each steam supply main has old Gorton No 1 air eliminators (3/8" fittings) at the front of the house where the supply mains turn 90 degrees down and join the wet return line. One of the supply mains is just getting warm to the touch and the 3 risers and radiators on this supply line are ice cold. On the 2nd supply main I was able to remove and clean the air eilimator and it is working and the piping is hot and the radiators on this supply main are getting hot.
It was difficult to remove the single old air eliminator and I am wondering if there is a way to clear / clean the other air eliminator or any other diagnostics I can do now in the middle of the heating season to try to get heat to the cold radiators. I have changed the air vents on the 3 radiators and verified tha the radiator values are operational and fully open.
Other maintenance I have done. - the hartford loop has a faucet drain at the end of the wet return near the boiler and I drained the wet return - some rusty water and then clear water after 10 minutes draining.
There are 2 additional steam mains from the boiler to the rear of the building and the
air eilimators were replaced when the boiler was changed. All the other radiators in the house except 3 are working properly.
0
Comments
-
Old houses settle
The house may have settled over the years, make sure that cool main has got some slope to it.Check it in relation to the other mains, It should be about 1 in of slope for a 10 ft run. Check the radiator runouts for proper slope also.
The only way I've ever cleaned an air vent is by boiling it in vinegar for 10-15 minutes, depending on what kind of thread sealant they used it can be tough getting them out. When installing them i use PFTE paste and or teflon tape - they come out really easy next time around.
Varivalves are very aggressive, try closing the working radiator vents down to the low setting and see if you can force steam down the cool main.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
main steam line venting question
Thank you for the suggestions
The 2 supply mains run side by side and are at the same level when they join the wet return. One gets hot and the other just warm. I will wait for a warm spell before getting someone to remove the air eliminator. I don't want to have it snap off and then have no heat. I ordered replacement Gorton No 1 valves. With the adapters, it will be tight installing the new ones due the thread size difference.
I will put the vari valves on their lowest settting to see if i can force steam into the cold radiators. Should I remove the radiator steam vent on one of the cold radiators to see if I get any steam ?0 -
It's worth a try
Just make sure you can kill the boiler if steam starts to billow out of the open vent tapping.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements