Main Vent Spitting out Water
ALIGA
Member Posts: 194
Few weeks back new steam boiler installed.
Noticed a few things, and now it makes sense:
- loosing water from boiler
- hearing alot of air coming out of 3-4 radiators fed from this main
- alot of dirt in the sight glass.
Today I notice water coming out of one of the gortons, alot of water, the gorton is a few months old. could the main and return have dropped a bit? before the new boiler went in, I did not have this issue.
Can I jack up the main and return an inch? Thoughts and guidance are welcome. thank you all.
Noticed a few things, and now it makes sense:
- loosing water from boiler
- hearing alot of air coming out of 3-4 radiators fed from this main
- alot of dirt in the sight glass.
Today I notice water coming out of one of the gortons, alot of water, the gorton is a few months old. could the main and return have dropped a bit? before the new boiler went in, I did not have this issue.
Can I jack up the main and return an inch? Thoughts and guidance are welcome. thank you all.
0
Comments
-
Repitching the main?
Check it with a level first. If you have to repitched it, what else will move if you jack it up?
I suspect your pigtail, or pressuretrol is allowing the pressure to get too high. An accurate 0-3 psi gauge would tell you when the pressure gets out of control.
Was the boiler cleaned after installation? Do a search for skimming.--NBC0 -
Main repitch
Hi NBC, i have a 5 psi guage, and the boiler shuts off around 1.5 - 1.7 psi.
I skimmed it on Sunday.
From the piping pic, can you tell if it is a parallel or counterflow system?
Shouldnt the excess water go back to the boiler via the lower return?0 -
Looks like it is a parallel system
I jacked the end of the main/return a little less than 1/4 inch.
Water stopped spewing out the vent.
Return has a slight pitch back to boiler. Main has a slight pitch away from boiler.
Hopefully this does the trick.0 -
Glad to Hear It's Working Better
I'd re-insulate that main so it's not generating so much condensate.All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements