Main Vent decision
TraderJay
Member Posts: 4
Hello all, I need some help with choosing the correct main vent. Background: Victorian house 3000 sf (14 radiators total) but, I have 3 on the 3rd. floor closed / old American Standard boiler / 31 ft. long main 3" diameter. Right now there is only (1) Hoffman #75 10 psi. at the very end of the main. Boiler sits toward the front of the house, main going to back of house. Can I use a Vent-Rite #75 5 psi. or stick with the Hoffman #75 ?
0
Comments
-
Too small
A 31ft long 3" main contains 2.6 cu ft of air, a Hoffman 75 is much to small and the Ventrite would be worse. The Hoffman 75 is rated at 0.5CFM while the Ventrite 75 is rated at 0.19cfm.
I suggest building an antler with 2ea Gorton #2's and the Hoffman 75 to vent that air FAST. The Gortons have a 1/2" thread so you will need adapters if using 3/4 pipe to build the antler.
The boiler pressure should be 1.5 PSI or less for efficient operation.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements