Weil pump
targetman
Member Posts: 105
Anyone ever worked on a Weil 4100? I'm dealing with one and it's the only one I have ever seen.
0
Comments
-
?
What's wrong with it?0 -
won't shut off
First off it's a duplex pump, but only one pump is piped and being used. This is not my account so I don't know the normal operation of this pump. I was sent today to change the motor and seal. This is no Watchman. The impeller looks more like a sprocket. It's flat and about a 1/4" thick. The seal is a lip seal. The replacement motor was 1/2 hp and the original was 1/4. After the repairs were made, I placed it back in service. First thing I notice is how loud it operates. The janitor said he thought it was always loud. The tank was full of condensate so I wanted to see it cycle. I had yet to turn the steam back on so I did't think it would take that long. After about 10 minutes it was still pumping. I broke a union to verify. Pulled the motor and pump also. It was about two thirds full. Turned the heat back on and left for my dentist appointment. Got a call an hour and a half later. The still had not cycled off. Need some ideas for tomorrow.0 -
It's a turbine pump....
not a centrifugal. Turbine pumps are positive displacement pumps usually used for low flow, high head applications. They are very sensitive to wear, not like a centrifugal. I would check the condition of the impeller and cases. If they are worn, the impeller will spin but not pump. I would also check to see if there is a clogged strainer at the impeller's inlet. If it were me, I would consider a conversion centrifugal type pump kit to fit this receiver, or a whole new centrifugal type condensate pump set with tank and float switch.
Centrifugal type pumps can take a lot of wear and still pump.Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements