Gone for a header
Jrock
Jrock Member Posts: 11
Had a William son 200 ,000 boiler installed the contractor undersized the line coming out of the top of the boiler & also under sized the equalizing line . Now the boiler is overfilling w/ the auto feeder on & shutting down on LoW water w/ it off the boiler glass g. Water is surging 3" up & down in the first 2-4 min of firing . -----I looked at specs the proper size is 3" & min. 1 1/2. My q. Is I only have 2" stock for threading pipe is there a way to pipe it w/ two lines both 2" out the top of boiler to fix problem ( and no I can't find contractor anymore ) to have him repair it . Thanks
  • Mark N
    Mark N Member Posts: 1,144
    Supply Piping
    No. It needs to be done in 3 inch pipe. The diagram shown in the manual is the bare minimum. Better would be 2 - 3 inch risers into a 3 inch header. This will produce very dry steam. Also boiler will need to cleaned and skimmed to clean the water and produce a stable water line.
  • Mark N
    edited January 2013
    Return Line
    Looking at your pictures in seems that you have a return that runs along your wall. That pipe looks now to be above the water line of your boiler. This is no good. The "A" dimension needs to be 28". This needs to be addressed as it looks like steam can now get into this return line and cause water hammer.
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,919
    Which model do you have?
    I don't see a reducer on that riser, and it doesn't look like there's room for a bushing. Can you explain exactly how this is piped?
    I'd also like to see some more pictures of the return piping. Am I seeing a return coming from behind the water heater at about the height of the boiler? Was your previous boiler much taller than this one?
    It looks like you may have a long horizontal return run that's about a foot or so above the current water level, and that's going to cause all kinds of problems with getting steam out of the boiler and condensate back in.
  • Hap_Hazzard
    Not just water hammer.
    It can cause exactly the problem he is experiencing.
    Steamhead Member Posts: 18,292
    I think it's bushed down
    you just can't see it. This is basically the same boiler as the Weil-McLain EG series. We see very few of these installed correctly.
    Consulting
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,424
    You can buy the dies I am selling
    you can buy pre cut pipe and fittings too.
    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • Paul48
    Paul48 Member Posts: 4,469
    edited January 2013
    Closer
    I think if you look closer, that's a step in the foundation, not a horizontal pipe.
    I'll correct myself....you are right, the pipe goes to the right.
  • Jrock
    Dry return
    Old boiler was never a problem with that same Dry return. New boiler is a Williamson gsa200 nsp
  • Jrock
    Gsa200nps
    Williamson gsa200nsp
  • Jrock
    Sorry bad picture
    Yes it is a curb in foundation But the 1" dry return is running full lea nth of house on that ledge back too boiler ........ Worked fine for 20 years that way thanks for any help !
  • Jrock
    Reducer in jacket
    Reducer in jacket & I knw the boiler manual calls for 3" rise & header w/ min. 1 1/2 eq line
  • Paul48
    Measure
    Check dimension "A". Measure from the bottom of the floor joists to the normal water line of the boiler, then check it at the point it drops to return and make sure it is 28" minimum above the NWL.
  • Paul48
    Dry Returns
    They must also be pitched, or you wind up with condensate in contact with steam.
  • Hap_Hazzard
    It can't be.
    It's lower than the header, which should be at least 24". (Looks like about 30".) I'd guess the part we can see is about 12-14" above the normal water line. It should be at least 28" above the MAXIMUM water level.
  • Hap_Hazzard
    3" pipe
    You can build your header with pre-cut threaded nipples. You can go with the lengths that are already there. The fittings might be slightly longer, but it shouldn't be critical. If nobody sells them locally you can get them online.
  • JStar
    JStar Member Posts: 2,752
    Header
    Where are you located?
    I make custom nipples when needed.
  • Jrock
    That may be a good option if I can't find a shop closer iam in rock away N.Y. Queens SSS. Super storm sandy Took may old willy Mac boiler .
  • Jrock
    Checked out
    It close 28 dimemention A Is 271/2 " above nwl
  • Hap_Hazzard
    You mean like the header
    is close to 3"?
  • Paul48
    Jrock
    I can't explain why it seemed to work with the old boiler. Each boiler and system can have its own peculiarities.That horizontal run slightly above the water line is causing your dancing water line. It provides a place for the water to go as the pressure begins to rise in the boiler.The boiler pressure is normally higher than the pressure at the end of the system. What puts the lost pressure back at the end of the system is that 28" column of water. It adds 1 psi back.Without that, you don't get condensate back into the boiler.Your setup has created a water column much less than the 28", and the system is struggling to equalize. Get the near-boiler piping corrected, and drop that return and you'll be much better off.