low ambient control
Paul S_3
Member Posts: 1,286
Tomorrow I will be installing two Johnson control low ambient kits (fan control) for ar410a system...what is the best setting for it ....it has a cutout and a subtractive differential....
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
lo ambient
as with most stuff, it depends! But a good starting point is, cutout = to 95* condensing temp or about 290psig. cutin is also ,it depends. Anywhere from 335-400psig.0