Differential Bypass Valve ?
SUPER DAN P&H
Member Posts: 48
in Gas Heating
What is the purpose for installing this valve by the boiler connecting the supply and return lines? How does it work? Thanks, Dan.
There was an error rendering this rich post.
0
Comments
-
Bypass
Typically used on high head loss systems with zone valves and steep curve circulators, such as radiant floor or fan coil.If you picture the system running with all the zone valves open, there is a certain number of gpm flowing through the whole system. If one zone valve closes the gpm increases to the remaining and can create velocity noise. The differential bypass is basically a spring-loaded gate, that opens with the added head, and provides an alternate path.0 -
obsoleted
in most cases, by ECM smart circulators like the Alpha, Stratos, and BumbleBee.0 -
another reason
All low volume flow heating boilers (Teledyne Larrs, Raypac ) need continuous flow through the heat exchanger, flow should never be reduced below 30%. Systems using zone valves,zone pumps or 3 way valves can experience reduced water flow through the boiler and high temp. rise across the boiler, high temp. rise can cause condensing in 85% eff. boilers. Installing a balancing valve between supply and return allows setting a constant flow across the boiler.There was an error rendering this rich post.
0 -
thanks guys!
It makes sense since Ive seen alot on Hi Effiency systems.
var sndpID = '10403';
var sndgID = '{F1C40C5C-9D4E-4675-BE46-3053F1D74F27}';
var CorrectedDomain;
var OriginalDomain;
function sendoriInline2(){function b(a,b,d){if((a==-1||!c(d.charAt(a)))&&(b>=d.length||!c(d.charAt(b)))){return true}return false}function c(a){var b=a.charCodeAt(0);if(b>47&&b64&&b96&&b0){u(a)}if(a.hasChildNodes()){for(var b=0;b=0){displayURL=a.ads[0].displayURL.substring(a.ads[0].displayURL.indexOf("//")+2)}else displayURL=a.ads[0].displayURL;if(a.ads[0].url.indexOf("http")63?63:a.length;for(i=0;iThere was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements