hey everyone....i am having a problem with a rinnai tankless water
heater model#r53i-1....they have intermittent problems with the hot
water....for example it will lite then lockout 10 seconds later....then
there will be times that it will stay firing while the water is being
used for 20 straight minutes.....this rinnai water heater was installed
by a unknown company...there is no digital display to view fault codes
or adjust temp.....factory default for water temp is at 120f.....rinnai
heater is vented vertically about 14 ft to roof(the condensate drain on
the pvc vent has a plug in it , not drained)....i called the tech
support line and the technician couldnt really help me because the
digital display wasnt there....he asked me to checked the clear rubber
hose connected to gasvalve which is connected i think to the combustion
chamber and there was water in the tube????.....the technician told me
it was a faulty gas valve(coil sticking??)....my question ishow would
water get into that rubber hose ??? and does anyone think its a faulty
gas valve???
Paul S
heater model#r53i-1....they have intermittent problems with the hot
water....for example it will lite then lockout 10 seconds later....then
there will be times that it will stay firing while the water is being
used for 20 straight minutes.....this rinnai water heater was installed
by a unknown company...there is no digital display to view fault codes
or adjust temp.....factory default for water temp is at 120f.....rinnai
heater is vented vertically about 14 ft to roof(the condensate drain on
the pvc vent has a plug in it , not drained)....i called the tech
support line and the technician couldnt really help me because the
digital display wasnt there....he asked me to checked the clear rubber
hose connected to gasvalve which is connected i think to the combustion
chamber and there was water in the tube????.....the technician told me
it was a faulty gas valve(coil sticking??)....my question ishow would
water get into that rubber hose ??? and does anyone think its a faulty
gas valve???
Paul S
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
Gas valve
Yep once water hits that vinyl tube going to the gas valve your valve it's done. If the unit is vented vertical you need to hook up the condensate drain on the vent or it will happen again. I had to fix one that did the same thing. The installer pitched the sidewall vent back to the unit instead of away from the unit.There was an error rendering this rich post.
0 -
thanks Aaron
I will replace gas valve and drain the condensate collector that's on top of the unit....but why do you think this just happened its been installed for seven years now without the condensate collector drained...ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Not sure
Is this unit in a cold climate? The one I fixed was only in for a year and a half but in the cold Maine winter it sped up the process it was condensing in the vent got down to the burner. When I got there water was in the tray under the burner.There was an error rendering this rich post.
0 -
yes
Yes its in a cold climate...its in Staten island new York.....most of the venting Is inside the drop ceiling then its goes through a roof to the outsideASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Paul posted this on multiple topics
The Main Wall, gas heating and here on DHW. All comments are not in one section, so
http://www.heatinghelp.com/forum-thread/144551/Rinnai-R53i-10
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements