The lwco is overflowing the gas fired boiler (steam heat)
bob2013
Member Posts: 1
in Gas Heating
I have a relatively new boiler ( 2 years), with a low water cut off system , Mcdonnell PS802-24. The thing is working fine when the water is low, feel up half of that water line, stops, then feed water again, then stops then goes on again, ending up over-feeding the boiler that shuts of. I disconnected the water feeder, so now when the water is low, the LWCO tries to add water but will not be able. So add water, reset the LWCO, then the boiler works fine again. I would appreciate any help.
Maybe relevant, I found the voltage transformer ( 120 to 24vac) warmer than what it should be.
Thanks
Bob
Maybe relevant, I found the voltage transformer ( 120 to 24vac) warmer than what it should be.
Thanks
Bob
0
Comments
-
I'd first check the probe on the PS-802
if it's dirty it won't detect water like it should. But if there's that much dirt in the boiler, it will need to be flushed as well.
Where are you located? There's likely a good Steam Man near you. Try the Find a Contractor page of this site.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements