BSE Orifices from an old post #14329
Options
Hydronicolic
Member Posts: 18
A client of mine recently brought an article on Steam Supply Orifices to my attention, it was published back in 2003. It was Heating Help post # 14329 titled BSE Orifices. I found the article very interesting, however my knee jerk reaction is...how do you keep them from clogging. The author addresses the issue and swears that in 5 years, and over 1000 installations, he has not experinced any problems. Ten years later, as we begin this new year, I'm wondering if anybody out there has any experience, good or bad, with his concept?
0
Comments
-
Clogging orifices
The pressures in these systems should be very low, such as 2 ounces. The boiler will have been chosen to be not over-sized for the radiation, and piped properly, for dry steam.
Therefore, the low velocity of the steam will not pick up much debris, and try to force it through the orifice, which has a diameter larger than most radiator air vents. I wouldn't expect any clogging in this situation.--NBC0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 114 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements