High Capacity Main Air Vent
New_to_Steam
Member Posts: 4
I'm having issues with radiators not heating up and, I suspect the problem lies with the main air vents. There are two of them: Durst No. 4's with a 3/4" thread. One of them gets hot but, no air is being expelled. The other is completely cold. Can anyone recommend a good, high capacity main air vent? FYI, the cut-in on my boiler is 1 lb and the cut-out is 2.5 lbs. I recently replaced most of the radiator vents with Hoffman 1A's.
0
Comments
-
Vents
Gorton2. It's the highest capacity, and highest quality main vent.
You should also lower your pressure to a cut in of 0.5 and cut out of 1.50 -
High Capacity Main Air Vent
Thanks so much!0 -
How Long
are your steam mains, and what pipe size? This tells us how much air is in each main that we have to get rid of.
Gorton #2 is the biggest vent made today, but do you really need it?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Main Line Specs
One line is 37' from the boiler, the other is 27'. The pipes are 2.5 inches in diameter.0 -
Definitely Gorton #2 territory
on the longer main. For the shorter one, I'd use two Gorton #1 vents. This should result in steam reaching the ends of both mains at about the same time.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I'll give that a shot.
Thanks for your help!0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements