Riello pump pressure
Paul_11
Member Posts: 210
in Oil Heating
We are having a problem with a Riello 40 F20.
The oil pump pressure is supposed to be set at 178 psi and yet we can't t it higher than 110 psi.
We figured it was the pump but the new one is acting the same.
Does anyone have any ideas on what else the problem could be.
Paul
A Real Good Plumber, Inc
The oil pump pressure is supposed to be set at 178 psi and yet we can't t it higher than 110 psi.
We figured it was the pump but the new one is acting the same.
Does anyone have any ideas on what else the problem could be.
Paul
A Real Good Plumber, Inc
Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-0593
NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER
A REAL GOOD PLUMBER, INC
NYC LMP: 1307
O:212-505-1837
M:917-939-0593
0
Comments
-
Hmm
If you tried a brand new pump and still have same problem, I would try a new psi gauge. Also Riellos are not your average burner. Pump pressure should be checked at the correct setting on pump too (see manual) and burner should be running (flame on) while checking. Also do you have any type of oil limiting device on oil pump. In NYC we have a Dept. Air Resources (DAR) kit that limits pressure to about 100 psi. This page shows which port to check psi with.
http://www.thermopride.com/pdf/2%20stage%20io.pdf0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements