Munchkin 140 makes strange noises when it is 0 Farenheit or less outside
DABegley
Member Posts: 3
I have a munchkin 140 boiler that makes strange noises when it is below 0
outside. I think this is due to improper timing between the
circulators and the boiler. I have a radiant heating system with three
zones. When one zone calls for heat the zone circulator turns on. If
the circulating water temp is not high enough the main circulator turns
on, a few seconds later the blower turns on followed by the gas valve
opening and the boiler flame igniting. The boiler commonly shuts off the
gas then reignites. When the circulating water temp reaches the set
point the zone circulator continues to run, the main circulator turns
off, a few seconds later the gas valve shuts extinguishing the burner
flame and the blower goes into the purge cycle. When the circulating
temp fall too far the cycle starts again from when the main circulator
activates. The system has an outside temperature detector which raises
the circulating water temp the lower the outside temp is. When the temp
outside is below zero the system makes some grinding/knocking noises
just before the boiler flame goes out (after the main circulator shuts
off). I believe this is because the boiler temp shoots up in those
couple seconds between when the main circulator shuts off and the flame
shuts off. If the circulating temp is low enough the rise in temp isn't
enough to make noises but if the circulating temp is high enough the
boiler temp gets up very high and causes the noises. Does this sound
like a valid theory and should I locate a technician to adjust this?
Thanks. The boiler temp is set at 180 with a variance of 30 (the factory settings), is that too high? One of the zones has an engineered wood floor, the other two are vinyl or carpet. The highest water temp I have seen flowing through the pipes is 165, based on the temp gage on the water outflow pipe about a foot from the boiler. If I look inside the boiler after the noises are made and the boiler has turned off the temp on the control panel reads 200 or more. I could set the temp to 170 or lower which could reduce the temp overshoot. Thanks again.
outside. I think this is due to improper timing between the
circulators and the boiler. I have a radiant heating system with three
zones. When one zone calls for heat the zone circulator turns on. If
the circulating water temp is not high enough the main circulator turns
on, a few seconds later the blower turns on followed by the gas valve
opening and the boiler flame igniting. The boiler commonly shuts off the
gas then reignites. When the circulating water temp reaches the set
point the zone circulator continues to run, the main circulator turns
off, a few seconds later the gas valve shuts extinguishing the burner
flame and the blower goes into the purge cycle. When the circulating
temp fall too far the cycle starts again from when the main circulator
activates. The system has an outside temperature detector which raises
the circulating water temp the lower the outside temp is. When the temp
outside is below zero the system makes some grinding/knocking noises
just before the boiler flame goes out (after the main circulator shuts
off). I believe this is because the boiler temp shoots up in those
couple seconds between when the main circulator shuts off and the flame
shuts off. If the circulating temp is low enough the rise in temp isn't
enough to make noises but if the circulating temp is high enough the
boiler temp gets up very high and causes the noises. Does this sound
like a valid theory and should I locate a technician to adjust this?
Thanks. The boiler temp is set at 180 with a variance of 30 (the factory settings), is that too high? One of the zones has an engineered wood floor, the other two are vinyl or carpet. The highest water temp I have seen flowing through the pipes is 165, based on the temp gage on the water outflow pipe about a foot from the boiler. If I look inside the boiler after the noises are made and the boiler has turned off the temp on the control panel reads 200 or more. I could set the temp to 170 or lower which could reduce the temp overshoot. Thanks again.
0
Comments
-
Munchkin 140 makes strange noises when it is 0 Farenheit or less outside
Forgot to describe the noises, they are a banging/grinding sound. Not horribly loud but loud enough to hear on the first floor.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements