My Steam Boiler won't fire unless......
Portgas
Member Posts: 8
I have a 35 year old Utica PEG-187S steam boiler running on a millivolt system. The gas control consists of a Honeywell
VS820 with powerpile.
The boiler will not fire up unless I momentarily short the two wires going to the TH terminals on the gas control. Once the
boiler runs, it turns off on its own when the programmed temperature setting is reached.
The pilot light works. I checked all the wiring and the low water cutoff switch.
Can anyone suggest what may be causing this problem?
VS820 with powerpile.
The boiler will not fire up unless I momentarily short the two wires going to the TH terminals on the gas control. Once the
boiler runs, it turns off on its own when the programmed temperature setting is reached.
The pilot light works. I checked all the wiring and the low water cutoff switch.
Can anyone suggest what may be causing this problem?
0
Comments
-
Powerpile
The expert with powerpile systems can be found in the gas section. Try re-posting this there.0 -
Thanks
Thank you.
I posted my problem in the Gas forum.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements