I am about to install a few Mepco Steam Traps Model 40-515A and would like to know if they can be put in both the Horizontal and Vertical positions. Does this have any sort of impact on their performance?

Comments

  • Steamhead
    Steamhead Member Posts: 17,314
    These are "Float & Thermostatic" traps

    and the floats won't work if they are installed improperly. The Inlet tappings must be at the top, with the Outlet tappings on the bottom. 