Steady Water-Level Contest
JStar
Member Posts: 2,752
I propose an informal contest for the remainder of the winter. Who can get the steadiest sight glass level on a steam boiler on a new install. Here's my first entry. Sorry for the sideways video.
SMITH 8S3 with Carlin power burner firing at 120,000 input.
Double 2" risers. 3" drop header. One 2" main.
<a href="http://m.youtube.com/watch?v=DYNzAYjd5K8">http://m.youtube.com/watch?v=DYNzAYjd5K8</a>
SMITH 8S3 with Carlin power burner firing at 120,000 input.
Double 2" risers. 3" drop header. One 2" main.
<a href="http://m.youtube.com/watch?v=DYNzAYjd5K8">http://m.youtube.com/watch?v=DYNzAYjd5K8</a>
0
Comments
-
Difficulty
Jstar, had trouble watching your video on a PC, but it seems this link will work.
http://youtu.be/DYNzAYjd5K8
This is the only video I have of mine right now, I will have to do another. I think I took this the first week I fired up the boiler so I had a lot of skimming ahead.
https://www.facebook.com/v/10150510866966253
Sorry for the low quality facebook video.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Wow
I can't believe no one else has posted. I was hoping to see someone post who has a........ now I can't remember it.
Its a variant of the hartford loop that is said to produce really steady water lines.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Gifford Loop?
I'd lke to learn more about these myself...0 -
Gifford loop
Thats the one!Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
-
Wow
Has anyone here used this?And, if it is all it claims to be, why wouldn't everyone use it? https://78462f86-a-1c056b1f-s-sites.googlegroups.com/a/energysavingscience.com/www/articles/henrysarticles/HPACGiffordLoop.pdf?attachauth=ANoY7crY_BRyOtz4MqZyfPfWph5UCrrUSMSEPQ6t79jw-9431pCs2IeKpsKL7kaFn1EhDy-dSZbsngtlM0hcXlFzHdFktfwfbAlkghw15ebMbntNtzan_1R216CG0NlRDq5y-t1PfEoy8k_EQs6Dw-Q-VnHXbe9mcfzdN8BXn3vXVd3CXjOlhRMAX_eP3utYL-JJxKvoapUokYGGfLgomzqrjaSSIeEmDjA9EnWBCPGqtfVunSO_Pw9N75MwJ4GU_On3xhkPITgj&attredirects=00 -
I would, but...
Mine's not a new install, so it doesn't count.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Hmmm
I didn't realize thats all a Gifford loop was, was raising the connection. Though what i don't get is I thought having that above the water line risks water hammer?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
drips
Connecting drips above the water line risks that, but there's no way this puts the condensate in contact with live steam.0 -
Water line
I'm reviving this contest.
http://youtu.be/C1NJ0oDRsss
Smith 8S4 with Carlin Ez Gas. 4" drop header. Two 2" mains.
We installed a Gifford loop on the VECO job. The only quirk was needing the water feeder to kick in for a few gallons as the system steamed up. Water levels rock steady on both boilers.0 -
Header
Is this the unit that is sporting a 5" header? If so I call cheating.
You're making me want to rip out my Hartford loop and replace it with a Gifford loop.
Mine has never been near that steady.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Water level
The 5" header wasn't mine. It sure did look good, though!
The Gifford Loop was partially by accident. The new boiler water lines were about 10" lower than the old boiler. We kept the Loop connection and changed the name from Hartford to Gifford. I've found that with proper near-boiler piping, the Loop makes a very small difference in the water level.0 -
Gifford Loop
The purpose of the Gifford loop is to prevent cyclic fluctuation of the water line, where the condensate returns so slowly that a low water condition may occur mid-cycle but adding make-up water results in flooding once the system drains. It doesn't reduce bumping or surging in the boiler.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
1st day 5in header
First day 5 inch header
Replaced both warren Webster trap cages above watchman
& fired up
Skimmed for 2 hrs.
Building heated up within 10 min.
Not bad. Still needs more cleaning after running a while
http://youtu.be/YHoV2ts0X3A0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements