Bypass valve?
adambuild
Member Posts: 420
Happy Holidays Wallies! Quick question! I was reading the I&O manual for the new TT Prestige with Trimax control. It has a diagram for piping with zone valves and shows a bypass valve at the end. My two baseboard zones go out and back in 3/4" copper and the piping from the boiler would be 1" without primary/secondary. Will a 3/4" bypass valve be sufficient at the ends of the manifold to give the boiler enough flow?
Thanks, Adam
Thanks, Adam
0
Comments
-
P/S piping
I would suggest primary secondary piping instead of the bypass valve.
Probably about the same cost for either but bypass valves have a bad habit of sticking open. If you are worried about water hammer on the zones then go with a delta pressure pump on the zone side.
Just about every bypass valve I have seen in the last 10 years wasn't working.0 -
Thanks!
Hi Steve,
Thanks for the response. I've never used a bypass valve. I always pipe P/S. The manual however shows a bypass valve both ways, straight through and with P/S!? I guess I'll call TT tomorrow to see if it can be left out. Kindly let me know if you have any other thoughts.
Thanks again, Adam0 -
bypass
i think they recommending bypass valve for the purpose of setting pressure drop across radiators and as a result setting flow rate. Same as circuit setter.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
use a pressure-dependent circulator
pump direct, and don't worry about it. If it's 110, consider replacing the internal circ with one.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements