Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Navien parts confusion

Options
Jack1124
Jack1124 Member Posts: 1
What happens if a gas pressure switch is accidentlly installed in place of the air pressure switch in a navien boiler.

Comments

  • HDE
    HDE Member Posts: 225
    Options
    Runs bad

    The switches have a different spring resulting in a different DC feedback to the board.

    Short of a big backfire causing damage just install the correct one and move on.
This discussion has been closed.