Steam boiler heating issue
Cerberus
Member Posts: 9
in Gas Heating
I recently purchased a home that has 1994 Burnham IN5 Steam boiler that worked fine until the last month...
Under the normal operation you can hear click as the cycle begins, pilot
flame comes on, then ignition begins, usually 10 sparks, after which
gas valve opens as heat boiler kicks in... Recently boiler randomly
stalls... thermostat calls for the heat, pilot flame comes "ON", ignitor
(electrode/flame sensor shown in picture) only sparks 3 times before it
goes silent after which loop ends... thus no heat... it might takes
minutes or hours for heat to kick back in by itself or another solution
is to manually restart which can also take few tries.
I am trying to figure out whats the problem, module or bad electrode?
Any help would be great,
Thanks a lot
K
Under the normal operation you can hear click as the cycle begins, pilot
flame comes on, then ignition begins, usually 10 sparks, after which
gas valve opens as heat boiler kicks in... Recently boiler randomly
stalls... thermostat calls for the heat, pilot flame comes "ON", ignitor
(electrode/flame sensor shown in picture) only sparks 3 times before it
goes silent after which loop ends... thus no heat... it might takes
minutes or hours for heat to kick back in by itself or another solution
is to manually restart which can also take few tries.
I am trying to figure out whats the problem, module or bad electrode?
Any help would be great,
Thanks a lot
K
0
Comments
-
Is The
Pilot lit? and not switching to the main burner. Or the sparking stopping before the pilot lites. If its the first [ pilot is lit ] clean the flame sensor. If the sparking is stopping check for debris's on pilot or bad spark wire.0 -
Pilot is
Thanks John for reply.
Yes pilot is lit, it always lights up...i thought thermocouple/sensor has something to do it... i assume alcohol should do a trick?
I have also noticed that pilot head is slightly tilted to the left side rather than centered on to the probe. Is it supposed to be straight and aiming on the the sensor or does this depends on the model? It look strange and not right.0 -
If it dosen't
Look right it probably isn't. Someone may have replaced the pilot with a non OEM. If you have to remove the pilot to clean I would have a professional do it. The pilot flame must contact the sensor AND be in the correct position to lite off the burners.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements