Quietside Condensing Dual purpose
Billjulian
Member Posts: 12
in Gas Heating
I have a slight rumbling on the 120DPW Quiestside condensing boiler. When the flame ignites. Maybe a slight delay in the ignition I don't know. Im a Rinnai guy. We got heat /HW but this rumble slightly shakes the unit for 1/2 second. Tech says not unsafe. Anybody have any ideas?
Thanks Bill
Thanks Bill
0
Comments
-
Likely too lean
You need to have it tuned with a combustion analyzer.0 -
Vent termination kit
We install Quietsides all the time, awesome piece of equipment. We started installing them about 6 years ago and have found the rumbling you describe on a few installs. The issue seems to arise from the vent termination that is provided with the Quietside. If you used the termination kit that came with the Quietside, I would start out by adding a piece of pipe (12-18") to the 90 for the air intake. If this stops the rumble, you have a few options. Let me know if this works and I'll give you a few recommendations.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements