fluctuating draft with power vent + power gas
TomM
Posts: 233
in Gas Heating
installed my own steamer, copying steamhead's combination of smith g8 and carlin power gas burner. Imitation is the best form of flattery.
-
I fired it up today for kicks. I'm trying to find a decent professional to come double check the burner setup before i call it quits for the winter. Anyway........
-
This has a Fields CV-4 power vent with outside air intake. The intake isn't connected yet. When firing, the draft fluctuates about .05" H2o, and i can't get it stabilized. The exhaust also has a pretty mean basslike hum, and i'm getting some type of pulsations.
-
I figure its because i used a 90 right off the boiler, and 2 more down the line. Not that that exceeds specifications for maximum flue length, but i'm getting some pretty mean turbulation going on in there I think.
-
anybody have experience with this? No matter what i do, i can't really get a stable draft reading over the fire, or at the breech. Damn power vents. I should have built a chimeny. I'm using Bacharach 125 digital analyzer.
-
Furthermore, i WILL consult a professional before i consider this set-upcomplete, and I have CO detectors, and I did stay at a Holiday Inn last night.
-
see pics
-
Thx-
-
I fired it up today for kicks. I'm trying to find a decent professional to come double check the burner setup before i call it quits for the winter. Anyway........
-
This has a Fields CV-4 power vent with outside air intake. The intake isn't connected yet. When firing, the draft fluctuates about .05" H2o, and i can't get it stabilized. The exhaust also has a pretty mean basslike hum, and i'm getting some type of pulsations.
-
I figure its because i used a 90 right off the boiler, and 2 more down the line. Not that that exceeds specifications for maximum flue length, but i'm getting some pretty mean turbulation going on in there I think.
-
anybody have experience with this? No matter what i do, i can't really get a stable draft reading over the fire, or at the breech. Damn power vents. I should have built a chimeny. I'm using Bacharach 125 digital analyzer.
-
Furthermore, i WILL consult a professional before i consider this set-upcomplete, and I have CO detectors, and I did stay at a Holiday Inn last night.
-
see pics
-
Thx-
There was an error rendering this rich post.
0
Comments
-
combustion number
sorry i forgot to post combustion numbers;
after run 10 min:
air set to 20 on burner. 105,000 BTU
CO 30ppm ok
O2 3.9 ok
stack 410F ok
eff 81.2 meh
Co2 9.7 ok
breech draft- -.15wc to -.02 mostly. sometimes i get positive numbers
-
-
after run 40 min:
CO 66ppm meh
02 3.8% ok
stack 421F ok
eff 81.3 meh
CO2 9.7% ok
breech draft -.20 wc to sometimes positive.
-
i listened around with a hose, and it seems most of the basslike noise is coming from the 90 right off the boiler. when i remove the plug for the breech draft testing port, it pulls air AND pushes air. ie, my meter is not broken, i'm definitely getting positive pressure at the port.
-
is there a better way to set up this exhaust? something is not correct.
Thx!There was an error rendering this rich post.
0 -
questions
Why the neckdown at the chimney entrance?
Is that other vent capped?0 -
thanks for the reply
the neckdown is because i am using a Fields Combovent 4", rated to 170,000 BTU. 6" is coming off the boiler. The power vent allows 65' of 5" at max btu, so my lengths are ok. The Combovent is only offered in 4" and 5". the 5" is up to 290,000 btu. My boiler is 105,000.
.
no, the intake is not capped. I will cap it and report my findings.
-
the power vent internal diagram is attachedThere was an error rendering this rich post.
0 -
getting somewhere
ok i think i have the following design problems:
-the power vent sucks way too much air, and my design causes a ton of internal exhaust turbulation, making the draft regulator swing excessively, causing fluctuations in my draft over the fire and at the breech.
-
I think a redesign with longer straight lengths and less 90's + two draft regulators should be in order.
-
man this power vent is a pain in the butt, the best reading i can get over the fire is about -.10 wc. if i get any closer to spec, there is not enough weight on the draft regulator, and it starts swinging causing fluctuations. If i turn the internal damper on the power vent less than 35 degrees open, then it whistles like a train. Motor speed controllers can't be used because the motor is capacitor start.
-
turns out this exhaust design is proving tougher than my fancy schmancy steam header.There was an error rendering this rich post.
0 -
Draft Regulators:
You need two draft controls and the PV is probably too big.
Where I work, you need a PV that has enough nuts to overcome 50+ MPH winds so you need two RC's.0 -
Power venter
Most power venters should have a damper control to adjust the venter because of all the different lengths of flues. The draft between the venter and the barometric should be no more than -.06"W.C. You can make a slide plate damper or neutral pressure adapter to adjust this but the venter should have its own damper.0 -
damper control
The power vent has its own damper. Any setting less than 35% open starts whistling.
-
i get it now. I need to set the power vent up to -.06 wc before i do anything else. Then, when the power burner is on, it should be simple fine adjustments to the draft regulator. If i can't get the reading between the power vent and the regulator down to -.06, then i need to add another regulator, and get the reading between the regulators down to -.06, (with the regulator closest to the power vent wide open, and the other one shut). At least that makes sense in my brain. Reality is another story.
-
i'm going to redesign for more straight lengths and less 90's, possibly add another barometric, and report back.
-
Thanks!There was an error rendering this rich post.
0 -
Intake roar
Not sure if this will be an issue on your system but years ago I was in a lab where a Carlin power burner was running. The overall system was quite loud. The engineer said, "watch this" He put a 1' long piece of 4" pipe on the burner inlet and it quieted the system right down. That was a long time ago and the current burner may not require it, but it is worth a look.0 -
well well well
whaddya know. by moving the draft regulator a little farther down the line, so the exhaust gases are more stable, and turning the power vent damper all the way down to 10%, i can get a stable draft. I guess the turbulence was making it swing, making me pull my hair out. Whats left of it anyway.
-.01-.03 over the fire
-.04-.05 at the breech.
-
made a HUGE difference in acoustics too. purrs like a kitten. Thanks! tuning combustion this weekend and we should be good to go.There was an error rendering this rich post.
0 -
flue
what about that single wall flue pipe ?There was an error rendering this rich post.
0 -
Tom
Don't you just love the nuance of every little detail? Being forced to visualize something that's invisible (air) will make you question your sanity.0 -
A clear
If the draft is excessive, it can pull the flame right off the burner head. This is called "loss of retention" which can cause the flame to roar, and on an oil burner can cause a smoky flame unless you add way too much excess air. We had that situation on an oil-fired steamer some time ago, and when we got it straightened out the lady's oil consumption dropped by a third.
So with that installation and such a nice piping job, the whole system should purr.
I would, however, double-check that you have enough clearance between the wood framing and the flue pipe. If it's even close to the recommended minimum clearance, I like to use double-wall as an added safety measure.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements