zone issue

i need to replace a zone valve with a circulation pump. Does anyone know how I would go about wiring the pump to the t/stat?

thanks

Comments

  • unclejohn
    unclejohn Member Posts: 1,833
    Yes

    Get a RIB [relay in a box } Break your 110 to the circ. through the normally open contacts and wire the t'stat to the the 24v coil. Done.