Low Delta T
hrlevy
Member Posts: 19
I have just installed 2 old Fedders hot water unit heaters in my garage. I seem to get only a WDT of 5 degree. Could this be caused by the high of GPH flow.
If I lower the water flow will this raise the WDT??
If I lower the water flow will this raise the WDT??
0
Comments
-
need more...
info... Unit btu ? Pipe size? Length of run? Circulator size?0 -
addl info
Reznor 56K & older Fedders similar sized , 20' 3/4 pex to each unit, one Taco 00R 3speed set to low, water temp in 160F0 -
0
-
Low delta t
Could mean high flow.
Could mean small supply return pipe size.
Could mean poor heat transfer in the emitter itself
Could mean warm room low delta between heated space, and emitter.
Coiled mean poor heat transfer between emitter, and conditioned space (dirty fins coil ).0