Glycol heat loss
Garfield
Member Posts: 49
How much efficiency is lost by putting 30% glycol through a boiler like a Triangle Tube Prestige? I understand glycol is inferior at heat transfer. After lots of googling all I found was that you may need more feet per second through the exchanger.
0
Comments
-
30% glycol
Has roughly 93.5% of the specific heat that pure water does, so you need to pump about 7% more volume in order to transfer the same amount of BTUs.0 -
7% more than minumum flow?
So there's really no efficiency lost as long as you pump more water through the boiler? The 399k boiler has a minimum flow of 19 gpm at full fire so is this the number i need to use?0 -
minimum flow
Would be 7% higher as well, so your 19 GPM becomes 20.3 GPM. Is this piped with a hydraulic separator or closely spaced tees in a primary-secondary configuration? If so (and assuming you don't have overly restrictive piping in that loop) you can usually use a 0010 or a Series 100 with the 399.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements