2 stage burner?

Options
These pictures are from the Weil McLain LGB-6 boiler that services my church. We're hoping the boiler can be set up for two-stage firing. From an earlier thread (here:  <a href="http://www.heatinghelp.com/forum-thread/143498/Zone-valves-on-steam">http://www.heatinghelp.com/forum-thread/143498/Zone-valves-on-steam</a>) it first sounded like it did- then perhaps did not- have a two-stage burner. Evidently, they are standard on current LGB-6 and above, but this is a bit older (1994) and the pictures posted left room for doubt.

Here's some additional pictures. Boy, those "High Low" wires sure have me hoping that this is a two-stage burner. Can anyone confirm?

Thanks,

Patrick

Comments

  • gerry gill
    gerry gill Member Posts: 3,078
    Options
    looks like the correct

    low fire valve to me.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Patrick_North
    Patrick_North Member Posts: 249
    Options
    Awesome!

    That's a relief. We're hoping this will help with a zoned system where one of the zones is about 1/3 of the boiler's EDR- pressure builds really quickly and short cycles. I'd love to see them pull out the zone valves, but the two zones are two separate buildings. If running this boiler with two strages will help significantly it seems like making the best out of a lousy piping situation.

    Thanks for the help, Mr. Gill.

    Patrick
  • Dave in QCA
    Dave in QCA Member Posts: 1,786
    Options
    2-stage test

    You could pull off the redwire on the Hi terminal on the gas valve and see what effect it has.  This would confirm that it will in fact give you two stages.   



     I forget what pressure you're running, but "normally" the set up would be to add an additional pressuretroll or vapor stat, depending on the pressure you're running.  You would run the red wire up to the new control, and a new wire back down to the gas valve.  It should bet set for a range that is lower than the cutout on the operating control.  This way, as the pressure rises, most likely caused because of only one zone being open, the boiler will drop into low fire and stay there unitl the pressure drops low enough to go back to Hi fire, or call for heat is satisfied. 
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com